110.3B would not allow a 230 v motor on a 208 volt system. And NEMA has a voltage tolerance of +/- 10 %. 208 volt motors are labeled 200V
:thumbsup:I see the disconnect
I am assuming constant speed/slip with only v decreasing
kwired is assuming constant load with v decreasing and slip increasing
since slip ~ torque and torque ~ current (power)
current would increase
110.3B would not allow a 230 v motor on a 208 volt system. And NEMA has a voltage tolerance of +/- 10 %. 208 volt motors are labeled 200V
I am generally inclined to agree with you. however, many 230V 3 phase motors are labeled for 208V. If this one is not, it may be a simple mater to just replace the motor.
And in this case we are talking about an impeller pump so there is a lot of fudge factor allowance.I see the disconnect
I am assuming constant speed/slip with only v decreasing
kwired is assuming constant load with v decreasing and slip increasing
since slip ~ torque and torque ~ current (power)
current would increase