NEMA motors or IEC motors?
NEMA motors can have a "Service Factor" of 1.0, 1.15, 1.25 or 1.30 (most are 1.15). The OL protection curve starts at a "pick-up point" of the curve, meaning the point at which the device BEGINS to respond and should trip in 2 hours at that level. For a motor with a 1.0 Service Factor that pick-up point can be 115% of FLA, for motors with a 1.15SF it can be 125% and for "Mill Duty" motors with a 1.25 or 1.30SF it can be 140%. The other end of that curve is the 600% level, so either 5, 10, 20 or 30 seconds depending on the Class 5, 10, 20 or 30. The shape of the curve in between is determined by I^2t (current squared x time). The vast majority of Off-the-Shelf NEMA motors are Class 20 with a 1.15SF, but submersible pumps are usually Class 5 or Class 10 and 1.0SF, some OEM machines intended for intermittent duty, like compressors, are sometimes Class 10 and 1.0SF as well. When any motor is run from a VFD, it is 1.0SF and Class 10.
IEC motors follow the same curve, but there is no Service Factor, they are all essentially 1.0SF and Class 10, with the pick-up point able to be between 115% and 120%, most brands of OL settling on 117%, the other end being 600% for 10 seconds.