What have you checked/measured so far?We have an 18.5kw abb motor which is used for blower application in preheater.
The motor draws ~20A current, well below rated current of 32A but still its temperature is rising above 85deg Celsius.
Two motors have burnt this month.
Help me solve this problem.
What have you checked/measured so far?
OK. I assume currents, voltages, and winding resistances were balanced and within spec?Current, voltage at motor terminals, motor temperature, winding resistance.
I can measure if you need anything else.
OK. I assume currents, voltages, and winding resistances were balanced and within spec?
Is the 85C winding temperature? That doesn't seem terribly excessive to me. But then I'm used to class F insulation with a class C rise.
Preheater suggests a cement works. If so, is the motor ventillation getting clogged up?
Is it a fixed speed application?
... is the motor ventilation getting clogged up?
...
Current 20.8, 21.2, 21.4A
Voltage 404v, 408v, 412v
Insulation class- F
I am using a temperature gun to measure the temperature. It even reached 100deg Celsius when run for 4 hrs.
Star delta starter is used.
An outlet damper to control the output air.
A shaft mounted impeller.
The requirement is to run it continuously for 4-5hrs which was working fine till this week when second motor burnt.
but due to this problem this week we are currently running it for 1-2hrs then letting it cool for an hour or so.
...Star delta starter is used..
That's fairly common in a lot of areas over there (India). Their grid is nowhere near as stiff as ours, they typically are required to use Reduced Voltage starting on anything above 11kW (which is a standard IEC motor size, roughly 7-1/2HP). Star-Delta is the lowest cost RV starter.Why?
Current 20.8, 21.2, 21.4A
Voltage 404v, 408v, 412v
Insulation class- F
I am using a temperature gun to measure the temperature. It even reached 100deg Celsius when run for 4 hrs.
Star delta starter is used.
An outlet damper to control the output air.
A shaft mounted impeller.
The requirement is to run it continuously for 4-5hrs which was working fine till this week when second motor burnt.
but due to this problem this week we are currently running it for 1-2hrs then letting it cool for an hour or so.
When you put your hand on the motor's cooling fins can you feel air flow?
whats in that black box upper left on floor?