Re: Motor overload control contact
It seem that the placement on of the overload on the grounded common side of a circuit is an acception. This does not indicate in no way that it is the preferred way in fact if the control wire leaves the cabinate it can not be on the grounded or neutral side. According to NFPA 78 8.4 you should never break the grounded common with a switch or contact.
Out of NFPA 79
8.3 Control Circuits. Control circuits shall be permitted to be
grounded or ungrounded. Where grounding is provided, that side of
the circuit common to the coils shall be grounded Ungrounded control circuits shall be provided with an insulation at the control
transformer if alternating current or at the power supply terminal if
direct current.
monitoring device that either indicates a ground (earth) fault or
interrupts the circuit automatically after a ground (earth) fault.
Exception No. 1: Exposed control circuits as permitted by Section 6.3 shall be
grounded.
Exception No. 2: Overload relay contacts shall be permitted to be connected
between the coil and the grounded conductor where the conductors between
such contacts and coils of magnetic devices do not extend beyond the control
enclosure.
Exception No. 3: Class 2 low-voltage circuits in Article 725 of NFPA 70,
National Electrical Code shall not require insulation monitoring.
8.2.4 Exclusion of Switching Devices. The equipment grounding
(protective) circuit shall not contain any switches or overcurrent
protective devices. Links or plugs in the grounding circuit shall be
permitted if properly labeled or interlocked with the control circuits.