megloff11x
I stumbled over this question in a study guide for another test, but haven't seen it in any NEC published study guides. This other guide claimed that you should reduce the motor overload size if the motor uses power factor correction capacitors at the motor after after the overload. It seemed to indicate that if given a motor power (VA or W), efficiency, and power factor, you should:
Calculate the new motor & capacitor current with the appropriate efficiency, power factor, and VARs of correction, using the usual techniques.
Use this corrected current and multiply it by the 1.15 or other specified factor under Article 430 (I forget the subsection and left my book at home) to get the new lower motor overload current setting.
The PFC caps reduce the phase angle between the current and Voltage, and for a given Voltage, tends to reduce current through the overload, which is upstream of both. Hence an overload of the motor would occur at a proportionally lower current than it would have without the capacitors.
I've never stumbled across any NEC provided reference that went through this drill. It makes sense but I haven't found official sanction for the method.
Has anyone seen this, and is this an official NEC approved method?
Matt
Matt