Motor overload tripping

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
You should be able to read the B40 if they are properly installed. I do not see it. Flip top to bottom.
Yeah they are in the wrong way

I hate to think of what is allowing him to reset it. I wonder if the motor is fried at this point
 
Last edited:

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
Yeah they are in the wrong way

I hate to think of what is allowing him to reset it. I wonder if the motor is fried at this point
So, these should be flipped so that the ratchet wheel is facing inward towards the enclosure?

I wonder why they have worked all of these years the way they are in the picture?

Sent from my SM-G998U using Tapatalk
 

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
Those heaters don't typically go bad, Check to see motor FLA on the nameplate. Then there should be a chart inside that motor starter to say what heaters you use for that motor FLA rating. Get the heaters installed the right way. Amp clamp each phase as the compressor is running until high pressure cutoff. Highest reading right before cuttoff is what you want to note. make sure it does not exceed nameplate FLA.

You probably want to check what the pressure switch is set at. I find all the time that someone has jacked up the pressure settings because of poor peformance od some piece of pnumatic equipment. Usually it's to compensate for resistance to flow due to the piping/lines being too small.

Is this a single stage or a two stage compressor?
So if the pressure switch was jacked up, it would be taking too much current, I understand that. What should the pressure switch be limited to?

I don't know if this is a single stage or two stage. How do I tell?

I'm going to try and make it over there today. Thanks again for all this help, guys. Wish I paid more attention in my motors class during my apprenticeship but also didn't have a lot of hands on during it either.

Sent from my SM-G998U using Tapatalk
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
So, these should be flipped so that the ratchet wheel is facing inward towards the enclosure?

I wonder why they have worked all of these years the way they are in the picture?

Sent from my SM-G998U using Tapatalk
They didn't. They allowed current to flow while the motor was in an overload condition. Guessing. Do a smell test of the motor.
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
I don't know if this is a single stage or two stage. How do I tell?
A suingle stage will have all one size cylinders, a two stage will have larger (primary stage) and smaller (second stage) cylinders. Usually factory settings on a single will be up to about 120psi and a two stage 150 - 200psi but not always
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
Resetting these prior to a cool down can also destroy them. Particularly if done multiple times.
Maybe it's just the nature of my business, but most I've changed are because I needed a different rating due to some change of operating conditions, machine relocation, different voltage, larger/smaller motor etc.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Resetting these prior to a cool down can also destroy them. Particularly if done multiple times.
If they are reset prior to cooling down, the ratchet wheel may not be 'grabbed' tightly in the eutectic alloy (solder). The result is the wheel will turn freely so the overload relay keeps tripping. This condition can often be fixed by heating the thermal unit and then letting it cool.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
From what I was told, they had never been replaced, and since I thought they were the problem. I replaced them. When I did, I installed the new ones just as the old ones were, which is what you see in the picture. After installing the new ones, I depressed the red reset button in order for the motor to work.

It worked for a while but then started tripping again, just as the old ones were doing. It seems like the problem isn't related to the overload heaters because it's acting the same as when the old ones were in. It is an intermittent trip, and the owner was wondering if it had to do with high ambient temperatures outside.

I still need to get back there to get the nameplate info, etc.

Sent from my SM-G998U using Tapatalk
Unless the overload relay is jumper out, I don't see how the motor ever ran. The ratchet lever has to be held down by the gear on the overload element for the overload relay to close and let the contactor pull in.
That was one advantage of that overload design...you couldn't install them backwards and have the motor run like you can with the bi-metallic ones. Also, they take more time to cool before you can reset than the bi-metallic ones.
 

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
Photos from the owner
7d226c6c551c32fae853a6481994425d.jpg


Sent from my SM-G998U using Tapatalk
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Unless the overload relay is jumper out, I don't see how the motor ever ran. The ratchet lever has to be held down by the gear on the overload element for the overload relay to close and let the contactor pull in.
That was one advantage of that overload design...you couldn't install them backwards and have the motor run like you can with the bi-metallic ones. Also, they take more time to cool before you can reset than the bi-metallic ones.
It looked like from the picture ratchet lever was not contacting the gear the best I could see, it may have still been in the tripped position when the picture was taken, or as you said, the OL block was bypassed. But what would be shutting it down? Since the op said it was intermittent, I would say it was the relief valve stuck closed on the head or pressure switch, so it’s trying to restart with full pressure on the head.
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
Art. 430.32 (A)(1) provides the minimum overload (heater) protection based on % of FLC based on how well the motor is built. Art. 430.32 (C) gives you the maximum heater size that can be used if the lower selected heated fails to allow the motor to start.
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
What kind of max pressure is he trying to get out of it? There are ways to get the pressure up, but it involves knowing the tank working pressure, the integrity of the tank, the ratio of the belt drive, the relief valve pressure. Basically you have to put a smaller sheeve on the motor. Don't do it, you don't want the liability. Compressor tanks are deadly dangerous.

He's probably got flow issues in piping. Set the high limit to 175 and add a receiver (air tank) to the far end of his piping, or a surge tank on whatever he is running on compressed air and having a problem with.

And yes it is a two stage pump, I can see the intercooler
 

Joethemechanic

Senior Member
Location
Hazleton Pa
Occupation
Electro-Mechanical Technician. Industrial machinery
Oh btw, make sure nobody did away with the relief valve, and if the one that is there pops off below the working pressure of the tank. It will be made of brass and have a number stamped on it. It will look something like this 51PQk6AqqYL._AC_UF894,1000_QL80_.jpg

There is also an adjustable type, You probably want it to pop off at like 185 if you are setting the high limit on the pressure switch to 175
 