Have what I feel is probably a stupid question and I think I know the answer already but here it goes. When measuring line to line in a 3-phase system, what you've got is what you've got?. What I mean by that is if I measure line to line and my multimeter reads 209V, is the system running 209V or with the three phases is it 480V?
I've got a motor which its nameplate reads the following.
Voltage :208 - 230/460
Amps :5.7 - 5.4/ 2.7
The overload is adjustable from 2.2A-3.4A, set at 2.8A, which even if this was running 460V, would be to low based on the 125% from 430.32(A)(1). With a clamp on ammeter around one leg reads 3.2A after the initial instantaneous current jump. The overload just started tripping today, this machine has been in the building for about a year now and never had this problem that I know of.
I'm fairly new here but it seems to me that this overload device is sized according to a 460V system, which would be incorrect in our application. For now I've turned the device up to its maximum 3.4A and haven't had it trip for the last few hours. Appreciate any feedback.
I've got a motor which its nameplate reads the following.
Voltage :208 - 230/460
Amps :5.7 - 5.4/ 2.7
The overload is adjustable from 2.2A-3.4A, set at 2.8A, which even if this was running 460V, would be to low based on the 125% from 430.32(A)(1). With a clamp on ammeter around one leg reads 3.2A after the initial instantaneous current jump. The overload just started tripping today, this machine has been in the building for about a year now and never had this problem that I know of.
I'm fairly new here but it seems to me that this overload device is sized according to a 460V system, which would be incorrect in our application. For now I've turned the device up to its maximum 3.4A and haven't had it trip for the last few hours. Appreciate any feedback.