andinator
Senior Member
- Location
- Lilburn Georgia
What my situation is :
A 75 FLA 3 phase 208/120 motor driving a big aircompressor. In the motor control panel is 3 70A fuses (or are they?).
How I am told to wire it:
Run out of 1200A MDP with 3 #6 THHN CU to fused disconnect. Run 3 # 6 THHN CU to motor . Install a 50A breaker in the MDP. Install 45A fuses in the disconnect. Recieved call today saying perhaps we need a 60A breaker in the MDP.
How I figured it....
200A breaker in the MDP. Nonfused disconnect. # 4 wire throughout.
I'm a resi electrician who started doing commercial 1 year ago. How is my thinking wrong? I'm desperate to learn. Will it work how I'm told to wire it?
Thanks
A 75 FLA 3 phase 208/120 motor driving a big aircompressor. In the motor control panel is 3 70A fuses (or are they?).
How I am told to wire it:
Run out of 1200A MDP with 3 #6 THHN CU to fused disconnect. Run 3 # 6 THHN CU to motor . Install a 50A breaker in the MDP. Install 45A fuses in the disconnect. Recieved call today saying perhaps we need a 60A breaker in the MDP.
How I figured it....
200A breaker in the MDP. Nonfused disconnect. # 4 wire throughout.
I'm a resi electrician who started doing commercial 1 year ago. How is my thinking wrong? I'm desperate to learn. Will it work how I'm told to wire it?
Thanks