My drawings have the following information, and I'm trying to figure out how the engineer came up with this breaker size.
Exhaust Fan - 40 HP, 52 FLA, 480 V, 3p - 125A Breaker
I get, 40 HP , In 430.250 - 52 Amps, 52 x 250% (430.52) = 130 Amps, In 240.6 (A) - Breaker size 150 Amps
Am I correct?