About 6 months ago I was called out to check on a 3hp 3ph pump motor @ a propane plant. The motor had tripped the overloads so I reset and checked the current under load. The motor current was way below the nameplate FLA but one of the phases was about 12% higher than the other two. The motor was replaced by another company today (not electricians) and they told the plant operator it was not getting enough amps.
I went out and checked the motor connections, OK. I checked voltage, AB=251 AC=249 BC=249 AG=129 BG=128 CG=218. It's a 120/240 3ph delta system. The motor is a wierd size 3 1/2 HP with a nameplate rating of 13.4 FLA at 230volts. I measured the current A=7.6 B=8.4 C=7.6 amps. There was very little load on the motor so I was not suprised except for the middle phase being that much higher. Is this within normal limits or is there a problem somewhere?
The pump seems to be operating OK.
I went out and checked the motor connections, OK. I checked voltage, AB=251 AC=249 BC=249 AG=129 BG=128 CG=218. It's a 120/240 3ph delta system. The motor is a wierd size 3 1/2 HP with a nameplate rating of 13.4 FLA at 230volts. I measured the current A=7.6 B=8.4 C=7.6 amps. There was very little load on the motor so I was not suprised except for the middle phase being that much higher. Is this within normal limits or is there a problem somewhere?