Read 430.6(A)(1). This tells you that the 430 table values must be used based on the horsepower rating of the motor, NOT the FLC from the motor label. Without the horsepower rating, you have no idea how to wire this motor. There should be a horsepower rating somewhere. Of course the next sentence tells you that if the motor is only rated in amperes, then you may extrapolate the horsepower from the ampere rating on the label. Thus the never ending circle begins. You must use the horsepower rating to determine the FLA unless it is not given, then you can use the FLA to determine the horsepower. Don't you love the code?