tryinghard
Senior Member
- Location
- California
I looked at an air compressor motor the other day that has a nameplate:
240V, 1ph, 1.5 hp, & 9.7A.
It was tripping a previously replace solid-state overload, Furnas brand, even though the LRA was 13.5 & FLA 12 to 11. As it turned out the overload is for 3ph and it has phase loss protection so it would not hold past 3 seconds. So we will be replacing it with a single-phase overload.
I did not have a megger with me but I did take an ohm reading between the motor leads and it is 1.5 ohms. Shouldn't the ohm reading between the motor leads be near 24.7?
240V, 1ph, 1.5 hp, & 9.7A.
It was tripping a previously replace solid-state overload, Furnas brand, even though the LRA was 13.5 & FLA 12 to 11. As it turned out the overload is for 3ph and it has phase loss protection so it would not hold past 3 seconds. So we will be replacing it with a single-phase overload.
I did not have a megger with me but I did take an ohm reading between the motor leads and it is 1.5 ohms. Shouldn't the ohm reading between the motor leads be near 24.7?