I've got an issue with a motor that I'm hoping someone more knowledgeable than I can shed some light on.
It's a 3 phase 208V motor for a compressor. The nameplate rating is 38.4A. It is being fed with #8 THHN and the panel is approximately 100' away. I was called because they were having issues with it and the tech from Ingersoll-Rand requested I come out and and look at the feed side of things as he could not find an internal issue.
While it was running I got readings of A- 29.7A, B- 23.5A, C- 18.9A. Voltage was consistent at the panel lugs and the breaker at A-B 209.4, A-C 209.9, B-C 205.3. These voltages held steady both under load and unloaded. All connections were secure and there were no signs of overheating or corrosion. The panel this is being fed from is practically a dedicated panel with only a lighting circuit and a circuit for a tube heater in it.
To me it seems that it is obvious that the problem is in the motor but for some reason the engineers keep looking to the premise wiring as the culprit. What am I missing?
It's a 3 phase 208V motor for a compressor. The nameplate rating is 38.4A. It is being fed with #8 THHN and the panel is approximately 100' away. I was called because they were having issues with it and the tech from Ingersoll-Rand requested I come out and and look at the feed side of things as he could not find an internal issue.
While it was running I got readings of A- 29.7A, B- 23.5A, C- 18.9A. Voltage was consistent at the panel lugs and the breaker at A-B 209.4, A-C 209.9, B-C 205.3. These voltages held steady both under load and unloaded. All connections were secure and there were no signs of overheating or corrosion. The panel this is being fed from is practically a dedicated panel with only a lighting circuit and a circuit for a tube heater in it.
To me it seems that it is obvious that the problem is in the motor but for some reason the engineers keep looking to the premise wiring as the culprit. What am I missing?