I have a 300 HP motor on a baghouse with a control cabinet. Based on the contactor, I thought it was a across the line starter however I behind the control board I can see some heat-sinks and SCR notation.
It's an older drive and the only nameplate info is 360 amps input and 300 HP output.
My initial reaction was to check Code compliance per 430.122, however, it does not seem to be a true "variable speed drive".
In this situation where there is obviously some sort of soft start, should the conductors be sized at 125% of the drive nameplate and the disconnects at 115% drive nameplate & 300 H P rated ?
Previously the install was connected with a 400 amp fusible disconnect and 500 kcmil which seems undersized based on motor rules.