Can fuses be used as overload only No short circuit ground fault over current protection for motors? 430.32, 430.33, 439.35 does not say it.
The fuse makers may disagree.
I've found it makes for a good income selling replacement motors. I prefer typical overload set up, leaving fuses for SC & GF.
I dont get it. Post #1 question i dont see any reply
Well, your sentence structure leaves a lot to be desired.
I think you’re asking if fuses can serve as ONLY OL protection, but not short circuit or ground fault protection.
In my opinion, the answer is no.
Can fuses be used as OL protection? Yes, they can, in fact many people do that for smallish motors.Can fuses be used as overload only No short circuit ground fault over current protection for motors? 430.32, 430.33, 439.35 does not say it.
Agreed. I can't think of a scenario where the fuse is sized to provide proper OL protection but not SC and GF. This is before my 2nd cup of coffee, but I'll state that it's impossible.My point is that if the fuse(s) is(are) sized properly as OL protection, they will be providing defacto short circuit and ground fault protection. At least for the portion of the circuit downstream of the fuse(s).
A lot of unknowns here, so YMMV.
Correct. Ok. So then fuses can serve as OL and SC or GF protection or just SC or GF protection No OL for motors?