acrwc10 said:With the size of some of the closets I have seen "huge'' I don't think it should be prohibited if the closet is over a certain size. I worked on a house last year where the master closet was larger then the kids bedroom.
acrwc10 said:Also if you can put the panel into the pantry closet, aside from the clothing what is the differance.
stickboy1375 said:A closet is a closet,
j_erickson said:I'd guess that the inspector in the op would require fire terated studs on either side.
stickboy1375 said:Had to edit this one,
Art. 240.24 (D) Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.
acrwc10 said:When I first read this I tought you had put " Indigestible". In reference to the pantry.
acrwc10 said:When I first read this I tought you had put " Indigestible". In reference to the pantry.
petersonra said:Some time ago an EC in this area got his you-know-what in a sling because he was mounting panel boards on plywood onto concrete walls. The claim was that the plywood was flammable. I am not sure what the issue was exactly, maybe non-flammable materials required.
I gather that this was a common practice and was being passed by the inspectors.
Somehow he ended up getting additional scrutiny beyond what the other ECs got (I think I know why but it is not relevant) and ended up having to make a fair number of them non-flammable by painting them with some kind of coating. They even made him go back and redo a bunch of them that they had already passed, or so i was told.
steve66 said:Yes, fire treated plywood is required in many commercial buildings, but for an inspector to carry that over to a residential building is crazy.
The old green treated wood didn't need special fasteners, but the new "arsenic free" stuff (often called AC2) does. I have heard of it eating through standard bolts in a year (but that could be a big fish type tale). I think you have to use either stainless or coated fasteners.
roger said:John, wouldn't that mean all the boxes would have to be attached to Fire resistant lumber as well?
Roger
stickboy1375 said:If your not using pressure treated 2x4's, whats the difference between mounting plywood to the concrete vs untreated 2x4's?
JohnJ0906 said:We often will get the carpenters to build a small wall 6-8" away from the wall in an unfinished basement for the service. That not only allows wires to run behind it, but insulation as well.