Mounting height of PV inverter above grade when provisioned with MC4 connectors

Status
Not open for further replies.

RERoyA

Member
Many newer 3-phase PV inverters are provisioned with bulkhead mounted MC4 connectors that allow direct interconnection of PV string wiring. The MC4s are generally located on the bottom face of the inverter chassis facing downward toward ground level. Is there any NEC section/requirement that can/should be used to callout a minimum height for these connectors above the ground plane (earth/concrete grade)? Now that there are 1500V PV strings, it seems this would be a real safety concern, as MC4 connectors are plugged/unplugged (no current) often at commercial sites.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I'm pretty sure the answer is ... No. The NEC does not have minimum height requirements for inverters. The manufacturer's manual may contain something.
 

pv_n00b

Senior Member
Location
CA, USA
Seems like wire bending requirements are about all there are in the NEC. Typically the inverter manufacturer will have a minimum distance required under the inverter.
 