This question came up and I was curious and couldn't find a definitive answer..
If there is adequate room within a panelboard enclosure, is it permissible to install a relay or contactor in the panelboard enclosure ??
Thank you
I was about to say the same thing but you said it better.The thing to keep in mind is that as far as the NEC is concerned a panel-board is the bus bars and the overcurrent devices. (See article 408) They are designed to be mounted in cabinets covered by article 312.
That being the case why would we be prohibited from mounting electrical equipment in an electrical cabinet?
Even if it is allowed
I personally don't like to see this or go behind it when troubleshooting is called on.
I have one in an old panel on property now that I need to get out of there. Its not practical or safe to troubleshoot this contactor with the panel live. Try to get a meter on the control coil. Ridiculous.
Its in very tight clearence and buried in adjacent load wires from the surrounding breakers.
I see it as a cut corner practice. Someone coming along later will have to guess where it is if they are looking for it.
Its should be in a box and labeled as to what it is.
That's not true where alteration is expected for common use.As soon as I put a hole in the panel or enlarge one of the pre-punched ko's I have technically violated the UL listing.
That's not true where alteration is expected for common use.
I will as soon as you show me an in-use listed panelboard w/listed enclosure and cover that has no holes in the enclosure.Can you show us this exception?
AFAIK once you change it it's changed. AHJ can go ahead and accept it, but to be re-blessed by the UL, and pronounced listed again, it needs an on site UL inspection.That's not true where alteration is expected for common use.
It depends on what and how you change it... and a little common sense really tells you whether the listing is voided. With electrical distribution equipment, it is expected to have conductors not part of the listing enter and leave, is it not? If the listing includes an enclosure (integral or as an accessory) with no KO's, there is no way to put the equipment to use without making at least one hole. To say making that hole voids the listing would be ludicrous.AFAIK once you change it it's changed. AHJ can go ahead and accept it, but to be re-blessed by the UL, and pronounced listed again, it needs an on site UL inspection.
UL standards such as 508A, for industrial control panels, have details for 'rerating' enclosures when holes have not been sealed by components or fittings that do not comply with the original rating.To say making that hole voids the listing would be ludicrous.
When I said making that hole voiding the listing would be ludicrous, I did not mean the hole wouldn't be used for the proper termination of a raceway or cable.UL standards such as 508A, for industrial control panels, have details for 'rerating' enclosures when holes have not been sealed by components or fittings that do not comply with the original rating.
Ul says that their label has to do with how the item was manufactured at the factory, as soon as it is installed UL says it can no longer pass judgement on it based solely on its labeling.
When I said making that hole voiding the listing would be ludicrous, I did not mean the hole wouldn't be used for the proper termination of a raceway or cable.
Does your first statement apply to an installed product?
I think you can get factory mounted contactors in every brand panelboard.
It is pretty typical that at least a few of the panelboards we install in a new job will have contactors in them.