Residential backyard. I have drilled and tapped the 1/8" steel plate (spot welded to the post(s) intermittently) and bolted the panel to the fence. There will be ground rods along the fence line. Do I need to run the EGC through a 2" grounding clamp on the nearest steel fence post, or is the bolted panel installation enough of a bond for the fence?
The rows of woven 6" plate steel are not welded at every post.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If your panel support is welded to a post, and your panel mounting method is conductive, I can't see a clamp being any better.
 
LarryFine
Thanks for pointing me to this section of the code. And the AHJ that I could reach liked the idea of the post connected (directly, approved method) to the grounding conductor. 250.136 was spot on for the job. I had been perusing the section that applied to "metal fences" around substations. That wasn't doing it for me.
 