mounting switches and receptacles

Status
Not open for further replies.

boatfull

Member
I know at one time I seen a code article regarding mounting switches and outlets, in boxes weather it be metal or plastic, having to use machine screws. Does that article exist?
Thanks
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Guess I must have imagined it. Thanks all for the reply
Are you thinking of 250.8(A)(5) & (6) for grounding?


250.8 Connection of Grounding and Bonding Equipment.
(A) Permitted Methods. Equipment grounding conductors, grounding electrode conductors, and bonding jumpers shall be connected by one of the following means:
(1) Listed pressure connectors
(2) Terminal bars
(3) Pressure connectors listed as grounding and bonding
equipment
(4) Exothermic welding process
(5) Machine screw-type fasteners that engage not less than
two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less
than two threads in the enclosure
(7) Connections that are part of a listed assembly
(8) Other listed means
 