I have a 3-phase, 480V, 25hp motor. Its full load current is 34 Amperes. I want to provide a MPCB for branch protection of this motor. Since the service factor of the motor is 1.15, I am going with a MPCB having overload protection range from 35 to 45 Amps. But when I see NEC code (430.52), it says Maximum Rating or Setting of Motor Branch-Circuit Short-Circuit should be 175% for time delay fuses and 800% for instantaneous trip breaker. This got me confused that if I go with 35-45A MPCB then what happens to short circuit protection. Also, whether this is good enough to sustain the starting inrush current of the motor.
Please guide me if I am missing a point here. Thanks.
Have you considered a NEMA 2 combination motor stasrer in a NEMA 1 encosure? It will be supplied with a correctly MCP disconnect, starter, and OLR.
The MVP would be adjusted per NEC art 430-52 (C)(3) and the OLD configured per the motor FLA. If the OLR requires heaters to be installed there should be a chart somewhere mounted in the enclosure which illustrates the correct heaters to be installed.
Then you also must consider how the motor is to be controlled. Commonly you would have a contactor with a 120vac coil. You could supply external 120vac source or include a CPT in the enclosure itself. Then are you using 3wire control with a start stop pushbuttons on the cover or a remotely located push button station.
I bring the control up because you sem to be overlooking the relation of a common motor starter package on putting together you own. Are you making this more complicated than it needs to be?
You also mentioned a branch circuit. The combination starter would be protecting the circuit from that location to the motor. The, you have the cable feeding the combination starter for which you must provide a OCPD to protect the branch circuit.