- North Carolina
I have a 3-phase, 480V, 25hp motor. Its full load current is 34 Amperes. I want to provide a MPCB for branch protection of this motor. Since the service factor of the motor is 1.15, I am going with a MPCB having overload protection range from 35 to 45 Amps. But when I see NEC code (430.52), it says Maximum Rating or Setting of Motor Branch-Circuit Short-Circuit should be 175% for time delay fuses and 800% for instantaneous trip breaker. This got me confused that if I go with 35-45A MPCB then what happens to short circuit protection. Also, whether this is good enough to sustain the starting inrush current of the motor.
Please guide me if I am missing a point here. Thanks.