why....Wye ? wye connection is consider the most economical for small ?high voltage
transformer and

Delta-delta connection is consider the most economical for large to low voltage
transformer


thanks
 
why....Wye ? wye connection is consider the most economical for small ?high voltage
transformer and

Delta-delta connection is consider the most economical for large to low voltage
transformer
Interesting, considering Delta-Wye is probably the most common.
 
It's not a question of economics. The question of whether the secondary should be a Delta or a Wye is simply a matter of whether you need the neutral connection to serve the intended loads. Offhand, I can't think of a good reason to ever use a WYE on the primary side.
 
Those papers from OEM's are getting harder and harder to find, many OEM' sare also pulling operations and maintenence manuals for older equipment off thier websites.
 
why....Wye ? wye connection is consider the most economical for small ?high voltage
transformer and

Delta-delta connection is consider the most economical for large to low voltage
transformer


thanks

generally speaking, dry type transformers are delta primary.

so, it would be delta primary, and wye secondary.

delta secondaries are used mostly when a public utility want's to
save money on supply transformers.

you can start of with an open delta, centertap one phase,
and end up with 3 phase service using two xfmrs, instead of three.

when and if you need to increase the service capability, you can
add the third xfmr, and have a closed delta service. lot's of utilities
did this during WW2, when materials for xtmr's were at a shortage.


randy
 
Another reason that most North American utilities use grounded wye - grounded wye transformers with five-legged cores is that ferroresonance is not nearly as likely as with an ungrounded primary winding. Ferroresonance can be a problem when the transformer is served by a significant length of underground cable where one phase can become open either by switching or fusing. See http://www.mikeholt.com/technical.p...erroresonance and Its Effects On Transformers
 
Another reason that most North American utilities use grounded wye - grounded wye transformers with five-legged cores is that ferroresonance is not nearly as likely as with an ungrounded primary winding. Ferroresonance can be a problem when the transformer is served by a significant length of underground cable where one phase can become open either by switching or fusing. See http://www.mikeholt.com/technical.p...erroresonance and Its Effects On Transformers

Thanks for the link...very fascinating. I learned something new today. :cool:
 