Retired
Hi, I’m new here. Many years ago I had a contractor install a Mr Slim split system in my bonus room above my garage. I still haven’t finished the room so not using the unit yet but it does function. I was looking inside my fuse panel and noticed that the contractor did not hook up the white wire to the neutral bar. Just the 2 hot wires and the ground are hooked up. Shouldn’t this wire be hooked up? It’s just hanging there. The insulation was never stripped off so I know it was never hooked up. Any help would be appreciated.
 
The Forum rules state:
This site is designed for:

  • Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
* This NEC® Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.

Knowledge and the practical application of the National Electrical Code is an essential part of all electrical installations. If it's important for you to understand the National Electrical Code, then look no further.

That said, without going into detail I will say the installation is likely correct as those units rarely need a neutral (white) connection so it does not need to be connected.
 