Mr

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
may get corrected, but I can't think of any condition where the primary would be wye. Might be fed from a wye system, but X0 would not be used.
The secondary would depend on your needs, Wye or Delta.
(480vs 480/Y277; 240 delta; 480 delta; 208Y/120, etc)
 

jtester

Senior Member
Location
Las Cruces N.M.
Wye connections on the high side are common in higher voltages, 25 kv and 34.5 kv for example, they are less expensive, and a little more forgiving when subjected to high voltages. Wye connections are also more common in underground high voltage systems because they aren't susceptable to ferroresonance.

Jim T
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
jtester said:
Wye connections on the high side are common in higher voltages, 25 kv and 34.5 kv for example, they are less expensive, and a little more forgiving when subjected to high voltages. Wye connections are also more common in underground high voltage systems because they aren't susceptable to ferroresonance.
No argument there, but a transformer with a wye primary should have the neutral point left floating. Don't bond it or connect it to the source neutral or anything else.
 

jtester

Senior Member
Location
Las Cruces N.M.
LarryFine said:
No argument there, but a transformer with a wye primary should have the neutral point left floating. Don't bond it or connect it to the source neutral or anything else.

Larry

I'm not sure I agree, my GE Distribution Transformer Manual says that wye-wye should only be used on 4 wire primary systems, and then only if the system neutral and the transformer primary neutral are tied together, if not excessive voltages will develop.

I completely agree on wye-delta transformer banks with 3 transformers, but on others, the primary neutral should be solidly tied to the system neutral.

Jim
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Yes, wye-wye is different. It's basically three 1-phase transformers sharing a common conductor. It's the wye-Delta I was speaking about.
 