Re: MRI's and Article 517.13
Let me take a try at this and then you tell me what you think, okay?
You have made reference to 517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas.
First let?s look at what a Patient Care Area is:
Patient Care Area is any portion of a health care facility wherein patients are intended to be examined or treated. ??.. The governing body of the facility designates these areas in accordance with the type of patient care anticipated and with the following definitions of the area classification.
General Care Areas is patient bedrooms, examining rooms, treatment rooms, clinics, and similar areas in which it is intended that the patient will come in contact with ordinary appliances such as a nurse call system, electrical beds, examining lamps, telephone, and entertainment devices. ?? In such areas, it may also be intended that patients be connected to electromedical devices
Critical Care Areas are those special care units, intensive care units?? patients are intended to be subjected to invasive procedures
Wet Locations are those patient care areas that are normally subject to wet conditions while patients are present.
As outlined by the definitions I can?t see where a MRI or X-ray would fall under the Patient Care Area. Also look at the part of the definition that states;
How did I do with this explanation?