Re: MRI's and Article 517.13
I admit that my knowledge about health care facilities is not what it should be but I am working on this to get a better understanding of the code intent.
Dave?s post was addressing 517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas so I looked at the definition of Patient Care Areas as outlined in 517.02 of the 2005 cycle of the code.
As defined there are two types of Patient Care Areas and either or both can be a wet location.
When looking at the definition we see that in a General Care Areas there are some areas in which it is intended that the patient will come in contact with ordinary appliances such as a nurse call system, electrical beds, examining lamps, telephone, and entertainment devices. In such areas, it may also be intended that patients be connected to electromedical devices (such as heating pads, electrocardiographs, drainage pumps, monitors, otoscopes, ophthalmoscopes, intravenous lines, etc.).
Take not what is outlined above.
Then we have the Critical Care Areas. Those special care units, intensive care units, coronary care units, angiography laboratories, cardiac catheterization laboratories, delivery rooms, operating rooms, and similar areas in which patients are intended to be subjected to invasive procedures and connected to line-operated, electromedical devices.
By reading these definitions it is clear that there is a difference between a General and Critical care area but both are Patient Care Areas. In the Critical Care Area the CMP was sure to point out every room that applied to that portion of the Critical Area definition.
The CMP also added a part to 517 that clearly describes what an X-ray room is and the criteria is for wiring one. The only reference I can find in Part V that would lead me to believe that the X-ray room is an exam room is the reference found in 517.78 Guarding and Grounding. Part (C) where it states ?shall be grounded in the manner specified in Article 250, as modified by 517.13(A) and 517.13(B).?
Therefore I stand on my belief, until proven different, that a MRI or X-ray room is not a Patient Care Area
This belief is based on the fact that in a General Care Area it states ordinary appliances and a Critical Care Area we are trying to save a life. In a MRI or X-ray room we are taking pictures and not treating the patient.