kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
That breaker is listed as is though. If you had to supply that lead in the field that might be different as far as what you can or can't use for it.So just to throw this out there. GE afcis have the neutral tail made out of MTW and that's all it says for insulation type. Idk if UL considers a panel a machine and yes it isn't pulled in conduit but it does show a separate respected entity accepting a use for that wire where not installed in a piece of machinery or in a whip to a piece of machinery.
Some those GFCI's and AFCI's even have smaller conductor for this pigtail than what you might use if you were field installing them.