Alexis
- Los Angeles
Hello,
We just had an inspection in one of the cities around Los Angeles. They have all their own local codes and rules. Some of them could be reasonable and some are just funny. I'd apreciate any feedback!
The property is a 10 unit plus HSE (11 meters total). We upgraded the main panel to 400A (with main disconnect) the sub panel breakers are all 30A with 10awg feeders to each unit. Inspector demanded to have minimum 6awg and 60A per unit.
What is your opinion? If I'm reading the 230.79 and 230.80 right the 400A main disconnect is falling under this requirement and gives us permission to keep 30A down the stream for each unit. That's how at least we've been doing this for many other inspections.
The other correction was that if we are replacing the panels we have to replace the feeder to each unit and we can't keep using existing flex as a ground, like it was done in each sub panel before.
He told us also to remove gas pipe bonding that we installed between each gas meter..
Some ridiculous corrections that he added for local utility rules:
1. No main ground wire allowed in the main service disconnect to bond to the neutral. Has to be installed in one of the meter stacks.
2. No parallel service feeders (we have two sets of 3/0)
3. No LB on the service mast (we have added rings for utility to seal). When I asked how do you even do that 90 on the wall without a LB, he said "be creative".
I'd apreciate any feedback from you guys! Thanks!!