I have a service rated 1200 amps Meter bank, no main for a multi family dwelling, no main just 6 service disconnects to turn power for the entire building.
Back in 2016 I bought the mike holt library and on tap conductor he said the only fee can be tap, NOT
Service Wires.
so if you have the meter bank with six disconnect and the electrical contractor is tapping from the meter bank to all six services breaker which it’s all built in together than what protect the Srevive wire from overload.