Multi-Main Tie-Main (MTM) configuration -- (load analysis & breaker sizing question; parallel service entrance)

loganwest123

Member
Location
Central NC
Occupation
Electrical Engineering
Our team is currently working on an engineering analysis for a facility with a parallel service entrance using a Multi-Main Tie-Main switchboard configuration — two 3000A mains with a normally-open tie breaker, fed from separate utility transformers on the same secondary bus.

The question is around load analysis and overcurrent protection coordination between the mains and the tie.

During a planned transfer scenario where one main is opened and the tie is closed to allow one transformer to carry the full load — the combined load approaches the interrupting capacity of the tie breaker. We're looking at Eaton Magnum SB units (SBS630 series, 65kA @ 635V) for all three positions.

A few specific questions:
  1. When sizing the tie breaker in an MTM arrangement, is it common practice to size it equal to the mains, or should it be derated to account for the worst-case single-transformer full-load scenario?
  2. For the trip unit coordination — if the mains are set with a long-delay pickup at 100% and a short-delay of 6 cycles, what's the recommended short-delay setting on the tie to maintain selectivity without nuisance tripping during transfer?
  3. NEC 230.71 limits service disconnecting means — in an MTM arrangement where the tie is internal to the switchboard, does it count toward the 6-disconnect maximum, or is it treated as a feeder breaker on the load side of the service?

Any insight from those who've done the coordination study on similar configurations would be appreciated. Utility is 480V, 60Hz, facility is a data center — so reliability and selectivity are the primary drivers. Thank you.
 
For the trip unit coordination — if the mains are set with a long-delay pickup at 100% and a short-delay of 6 cycles, what's the recommended short-delay setting on the tie to maintain selectivity without nuisance tripping during transfer?
Why does the Tie need any over current protection at all?
If each main has the same settings and is expected to carry the entire load why would you want the Tie to open at all?
 