Multi motor discconnect size.

Status
Not open for further replies.
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
I have an existing 200 amp 480v disconnect fed with 2/0 cu.
We are increasing the total connected HP load on this service to 125.
2 - 50 hp
2 - 5 hp
5 - 3 hp

Increase wire to 3/0 and disconnect is rated @ 125 hp. Only the 3 hp motors start at one time. Very close.

Problem is the 5 - 3 hp motors are controlled via a 25 hp VFD. Do I use the actual connected HP to determine the minimum HP rating of the disconnect or include the full 25hp of the drive?
 
Tom, 430.122 says not less than 125% of the rated input of the drive for the conductors,

and 430.128 says disconnect shall be 115% of the rated input of the drive.
 