I was recently called in to evaluate a multiple building/multiple service (12.47kV delta - 480V/277Y 3P, 4W) facility that had an emergency generator (1500kw) installed to serve loads in both buildings.
The rub is 3-pole transfer switches were installed in both buildings. Short of recommending the replacement of all transfer switches with 4-pole switches is another solution available? I?m currently digging into 250.30(A)(4) as a last hope, or at least I have not been able to poke holes in applying it...yet. I?m open to anything you can throw at me (no sharp objects please).
The rub is 3-pole transfer switches were installed in both buildings. Short of recommending the replacement of all transfer switches with 4-pole switches is another solution available? I?m currently digging into 250.30(A)(4) as a last hope, or at least I have not been able to poke holes in applying it...yet. I?m open to anything you can throw at me (no sharp objects please).