Multi-Unit Dwelling Calculation

Status
Not open for further replies.

dav5y

Member
Location
NYC
Hi All,

I'm calculating the feeder size for a multi-unit dwelling. My question is, after I calculate VA and apply demand factors for general lighting and small appliance loads can I still apply the demand factors in "Section IV - art. 220.80" on the feeder ?????
 
No, the demand factors in Part IV (Optional Methods) would start with the total load, not the demand load figured from Part III.
 