A coworker argues with me that you can use a single neutral for two different current carrying circuits.
He wired up two receptacle 120v 20 ampere circuits each with its own 12 AWG THHN line “hot” leg connected to its individual breaker as normal but having the two circuits neutral leg spliced together sharing a common neutral with the same AWG wire size as a single line or “hot” wire
I redid his circuit to add an additional 12 AWG neutral to each individual receptacle to the neutral bus and remove the connecting splice because I figured if the two circuits were sharing a neutral and loaded up to max 80% of circuit rating then the neutrals in the circuit would be carrying 2x their max current
However, in a multi wire branch circuit with a 240 volt circuit relying on two hots and a neutral only to carry unbalance current it is clear that both hots carry close to equal current
However what I don’t understand is how code could allow a multi wire nm cable to allow both hot wires to return on one neutral for the explanation above if it’s a 120 volt receptacle circuits?
He wired up two receptacle 120v 20 ampere circuits each with its own 12 AWG THHN line “hot” leg connected to its individual breaker as normal but having the two circuits neutral leg spliced together sharing a common neutral with the same AWG wire size as a single line or “hot” wire
I redid his circuit to add an additional 12 AWG neutral to each individual receptacle to the neutral bus and remove the connecting splice because I figured if the two circuits were sharing a neutral and loaded up to max 80% of circuit rating then the neutrals in the circuit would be carrying 2x their max current
However, in a multi wire branch circuit with a 240 volt circuit relying on two hots and a neutral only to carry unbalance current it is clear that both hots carry close to equal current
However what I don’t understand is how code could allow a multi wire nm cable to allow both hot wires to return on one neutral for the explanation above if it’s a 120 volt receptacle circuits?