I think you guys are reading too fast
this has nothing to do about the neutral or EGC, and he doesn't mention that the #10 was ran for voltage drop, it might have just been what was already installed and wants to use it? I don't see anything in the NEC that would prevent him from using two #12 phase conductors and a #10 phase conductor to feed the hots to a MWBC circuit.
Sure now if this #10 was run for voltage drop then that is another issue if not run in a metal raceway.
Wow using a requirement for the EGC for a neutral then using a rule for a feeder for a branch circuit?
talk about mixing apples and oranges:lol:
Wayne, they are right, the code is inconsistent between branch circuits and feeders. A feeder neutral can't be smaller than required by 250.122 to cover short circuit current. By all rights, the branch neutral should be no different. The EGC would have to be #10 per 250.122(B), regardless of the reason for the #10 phase conductor. That's been true for several cycles.