dummycheck
- Texas
- Engineer
I'm working on a project where we're specifying multiconductor cable in a ladder style cable tray. As such, we'll be following NEC 392.22(A) and 392.80(A)(1). I've got a few questions about different parts of this code section. All the loads will be single phase 208V, so the cable will contain two current carrying conductors and a ground. We don't have a spec on the exact multiconductor cable yet.
For 392.22(A)(1), I think we should be able to keep everything smaller than 4/0. To get the cross sectional area, do I just add up the area of all the cables? Is there more to add for this if I don't have the exact cable we're using yet?
For example, we'll have 20 sets of (2) #2 AWG and #8 GND.
#2 = 0.067in^2
#8 = 0.017in^2
Total area = 0.067 + 0.067 + 0.017 = 0.151in^2
20 * 0.151in^2 = 3.02in^2
Per column 1 of table 392.22(A), I could use a 4in wide cable tray?
For 392.80(A)(1), there is a reference to table 310.16 which I'm familiar with, but also table 310.18 which I am not familiar with. I'm not really sure of those cable types, best I can tell they are just different insulation types? Are these common in multiconductor cables? Does the section reference this table just in case you're using these types or is there more to it?
Also, to make sure I'm reading 392.80(A)(1)(c) correctly, if you've got your cable spaced out as indicated you can use the equation in 310.14(B) which will allow you to calculate your ampacity, but this is not a requirement. It's just a way to get
#2 = 0.067in^2
#8 = 0.017in^2