Member
I have a question with regard to the 2005 edition of NFPA70.
Specifically 392.11- Ampacity of Cables, Rated 2000 Volts or Less, in Cable Trays.
Application: Type MC, multiconductor cable with not more than three current carrying conductors, installed in accordance with 392.9, in open ladder type tray.
Both 330.80(A) and 310.15(B)(2)(a) exception 2 refer to 392.11.
392.11(A)(1) applies the derating factors of 310.15(B)(2)(a) only to cables with more than three current carrying conductors.
392.11(A)(3) limits the ampacity to comply with 310.15(C) when spacing is maintained.
Question: Will derating factors apply to Type MC, multiconductor cable with not more than three current carrying conductors without maintained space in lengths exceeding 24 in.?
The wording, as I read it, does not require derating, though I suspect this is not the intent.
Your help will be much appreciated.
Specifically 392.11- Ampacity of Cables, Rated 2000 Volts or Less, in Cable Trays.
Application: Type MC, multiconductor cable with not more than three current carrying conductors, installed in accordance with 392.9, in open ladder type tray.
Both 330.80(A) and 310.15(B)(2)(a) exception 2 refer to 392.11.
392.11(A)(1) applies the derating factors of 310.15(B)(2)(a) only to cables with more than three current carrying conductors.
392.11(A)(3) limits the ampacity to comply with 310.15(C) when spacing is maintained.
Question: Will derating factors apply to Type MC, multiconductor cable with not more than three current carrying conductors without maintained space in lengths exceeding 24 in.?
The wording, as I read it, does not require derating, though I suspect this is not the intent.
Your help will be much appreciated.