Just curious, as I don't really see where this is explicitly defined. Say I want to have one 2 gang box that has a 120V 20 Amp circuit and a 240V 20 Amp circuit present. For safety, and convenience I would run a 3 phase breaker for these 2 circuits. I realize that common trip is not required, although handle ties might be a good idea, 3 phase breakers seem like an easier and perhaps safer way of accomplishing the same thing, as they are commonly available, and if 3 breaker handle ties exist I've never seen one, not that all breakers could even be tied that way between a single pole and a dual pole breaker, but anyway that isn't the real question.
The real question is what would be the grounding requirements for this? I know that if I was to run these 2 circuits in EMT no separate EGC is required but having one is a better practice. I know that if running NM-B, just running two 12/2 cables would be typical, however it results in non obvious color coding in the box where half the wires really should be reidentified. However, what if this was PVC conduit or a non-metallic raceway? Is one 12Ga ground sufficient or does there need to be an EGC return sufficient for a simultaneous fault of both circuits? Or could you feed this box with 12/4 NM-B? There only needs to be a single neutral going to this box, as the 240V doesn't need one. But what about ground?
I assume all non-metallic scenarios would be the same, regardless if it's NM-B or PVC or some non-metallic raceway like wiremold. I see in the NEC where non-metallic is defined, and see where handle tied breaker use is defined when 2 split phase circuits share a neutral, and also the grounding requirements for metallic conduit and raceway. What I do not see defined is the EGC requirements for multiple circuits sharing the same non-metallic path.
The real question is what would be the grounding requirements for this? I know that if I was to run these 2 circuits in EMT no separate EGC is required but having one is a better practice. I know that if running NM-B, just running two 12/2 cables would be typical, however it results in non obvious color coding in the box where half the wires really should be reidentified. However, what if this was PVC conduit or a non-metallic raceway? Is one 12Ga ground sufficient or does there need to be an EGC return sufficient for a simultaneous fault of both circuits? Or could you feed this box with 12/4 NM-B? There only needs to be a single neutral going to this box, as the 240V doesn't need one. But what about ground?
I assume all non-metallic scenarios would be the same, regardless if it's NM-B or PVC or some non-metallic raceway like wiremold. I see in the NEC where non-metallic is defined, and see where handle tied breaker use is defined when 2 split phase circuits share a neutral, and also the grounding requirements for metallic conduit and raceway. What I do not see defined is the EGC requirements for multiple circuits sharing the same non-metallic path.