electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
Hmmm why do gremlins keep sneaking in at night and changing the code book from the way it has been for decades?Not correct for a 2-wire circuit on a 120/240V system. See 240.15(B)(2).
For a 3-wire individual branch circuit for a 120/240V load, I'm unclear whether 240.15(B)(2) applies or not. For a 120/240V load on other than an individual branch circuit, the question is moot because of 210.4(C)--exception 2 is the only way to comply.
Cheers, Wayne