I have a question about using the derating factors for more than 3 current carrying conductors in a raceway. I have a situation where I need to run 11, 2 pole 30A circuits to power a piece of equipment. #10 is good for 30A based on 310.16. However, I now have 22 current carrying conductors in a single conduit, which requires me to derate the ampacity of the wire based on 310.15(B)(2)a. The #10 is no good any more and I have to drop to #8's. Which will still fit in my conduit. The question is, if the intent of 310.15(B)(2) is to constantly derate the ampacity of the conductors in a multiwire circuit as the number of conductors increase, then what good are the conduit fill tables?
For instance, take 1" EMT. Its maximum fill per Table C.1 is 16 #10's. A #10 per Table 310.16 is capable of 40A using the 90 degree column. If you apply the adjustment factor of 310.15(2)(a) assuming that 15 of the #10's are current carrying and 1 of them is the ground, the #10's ampacity is reduced to 20A. 20A is too low so the wire size must be increased.
A #8 has an ampacity of 55A using the 90 degree column. Half of 55A is 27.5A which is allowable. I now have to use 16, #8 conductors per the calculations. 16, #8's bumps me up to 1.25" conduit.
Am I missing something here? :roll:
For instance, take 1" EMT. Its maximum fill per Table C.1 is 16 #10's. A #10 per Table 310.16 is capable of 40A using the 90 degree column. If you apply the adjustment factor of 310.15(2)(a) assuming that 15 of the #10's are current carrying and 1 of them is the ground, the #10's ampacity is reduced to 20A. 20A is too low so the wire size must be increased.
A #8 has an ampacity of 55A using the 90 degree column. Half of 55A is 27.5A which is allowable. I now have to use 16, #8 conductors per the calculations. 16, #8's bumps me up to 1.25" conduit.
Am I missing something here? :roll: