Re: Multiple Feeders To A Single Building
I'm sorry for not laying it out completely for everyone.
Yes, the existing panel is located in an equipment closet at the classroom wing and does not have sufficient capacity (buss ampacity not breaker space) to add load to. It has a main circuit breaker installed to it.
The existing classroom wing is physically attached to a covered exterior open walkway that passes between this building and the adjacent buildings. The adjacent buildings are also physically attached to this walkway, but not to the classroom wing in question. So technically they are all attached, however, they "stand alone".
The main switchboard that feeds this existing panel (as well as the other building's panels) is located remotely from this classroom wing in an outdoor equipment yard.
In response to Charlie B's comments, are you saying that if the HVAC is fed 480 volt and the existing panel is fed 208 volt, I would fall under 225.30 (D) exception?
I am in California and we are currently using 2002 NEC (2004 California Electrical Code).
Thanks for all your input.