Multiple Fire pump- Electrical Load calculations

Hello,

Please see the attached SLD. We are upgrading the power for the entire campus. Each building on the campus has a 30 HP fire pump. FPB#2 is the board that will feed all the fire pumps.

The breaker size for each fire pump is based on the fire pump LRC, which is 240A.

My question: Since the fire pumps are being connected after the meter, should the service board be sized to include both the FPB load (720A) and the MSBH2 load (933A), for a total of 1,653A? In other words, does the MSBH2 board need to be rated for 2,000A? or are we ok with 1200Amps?
 

Attachments

  • Screenshot 2025-09-08 115151.png
    Screenshot 2025-09-08 115151.png
    44.7 KB · Views: 17
It seems to me the Main Switchboard [MSBH2] it is not the source but the “main consumers” SLD Fire pumps installation02.jpg
The main switch has to be-at least- 2000 A rated.
 
There should not be a main switch ahead of the meter other than the MV switch on the primary of the transformer.

You also should have a separate vertical section for the tap itself, or make sure you can fit both the tap and the meter in one section.

Speculating here, but could you do multiple taps, one per pump, and get rid of FPB?
 
Thank you, tjdilly for your remarks. I am not a Fire Pump protection specialist, indeed, and Chapter 6 of NEC- Chapter 6 Special Equipment- mainly art. 695 Fire Pumps-is not my domain of activity.
So, if the supply source is a transformer and for supervised location only-see art. 450.3- you don't need a secondary protection. According to art.695 (B) Conductor Size. and 695.5 Transformers the two switches from my above sketch are not required-even not permitted.
 