Re: Multiple GEC on one lug?
In essence you are only required to have one GEC. If there are other ELECTRODES available (soon to be "present" - '05), then you have 2 options.
1. Install the conductor(GEC) from the electrode back to the point of the first point of disconnect [250.64(F)... or to one or more grounding electrode(s) individually]. That conductor(s) will then be a GEC and has to remain unbroken and unspliced (250.64(C).
2. If using the cold water as your electrode, then it is to be SUPPLEMENTED[250.53(D)(2)].
This "supplemental" electrode is just that, supplemental, and can be bonded to a number of different locations as specified in
250.53(D)(2) The Supplemental electrode shall be permitted to be "BONDED" to the grounding electrode conductor, the grounded service conductor, the nonflexible grounded service raceway, or any grounded service enclosure.
There is an exception, but that exception is for industrial & commercial occupancies with supervised maintenance.
I do not see where this permits bonding to the cold water pipe (electrode) for any other occupancy.
The other electrodes that are available only need to be "bonded" together to form the Grounding Electrode System (250.50).