shortcircuit2
Senior Member
- Location
- South of Bawstin
Take a look at the 1-line diagram below. The diagram shows a layout of 3 single phase 120/240volt separate generators feeding one building with simple 2-pole transfer switches.
Would there be trouble with the generator electronics and a common neutral between all 3 units?
Is there any concern if standard 2-pole transfer switches are used and 1 gen-set were to loose a neutral or hot leg?
Should the set-up use transfer switches that break the ungrounded conductor making them separately derived?
Would there be trouble with the generator electronics and a common neutral between all 3 units?
Is there any concern if standard 2-pole transfer switches are used and 1 gen-set were to loose a neutral or hot leg?
Should the set-up use transfer switches that break the ungrounded conductor making them separately derived?