But Iwire...a neutral in a MWBC is from the same source...right?
So a hot in one MWBC would have potential to the neutral in another MWBC.
Yes.
The 3 gen-sets are seperate sources so there would be no potential to the other thur a interconnected neutral.
If the neutral of all three gensets were isolated there would be no potential between gensets.
But the neutral of all three (four really) are all connected so there is potential between the gensets (and utility) But that fact is not unsafe.