Re: Multiple ground electrodes
This might be better off in the Engineering section and I hope this does not sound like a DIY on the loose....
Getting away from the minimum code requirement of #6 to a driven rod and looking at making a very low impedance path to ground, what would be considered a more effective (cost vs. performance) driven ground electrode system:
1. A single driven rod and #6 (existing)
2. Two driven rods and #4 12 feet apart
3. Multiple driven rods, X feet apart in what sort of configuration- square box, straight line, Y- with a welded 3/0.
The building has a listed lightning protection system but the bond to the service entrance connects to a #6 existing driven rod. The foundation is a poured slab with plastic sheet vapor barrier and PVC water connection to the meter. The SE GEC (3/0) connects to the water system- 1200A service, TVSS on main - by running >100 feet in the attic. Lightning damage is a recurring problem and I'm thinking that the existing GEC has way too much impedance to carry the shunted voltage to ground, forcing the voltage to seek ground wherever it can find it.
I know driven rods are not the best grounds but that appears all the alternatives I have.