I'm looking at a site that has a pretty typical existing line-side tap, with 600A tapped on the line-side of a 3000A hot-sequenced switchgear/meter. I'm potentially trying to add up to 1600A of PV as a Phase 2 addition.
1) Assuming there is room in the gear, my Plan A would be to install a second line-side tap. I don't believe there's a any Code issue with this?
2) If there is no room in the existing switchgear, I don't believe I can add a tap-box in front of the switchgear because the existing 600A tap would become a tap of a tap, which is a violation?
3a) I'm thinking I can add a new main switchgear in front of the existing gear. Say a 5000A bus with a 3000A main, a 3000A branch feeding the existing switchgear and a 1600A branch feeding the new PV system. I'm not sure if this would strictly meet 705.12(D)(2)(3)(b)&(d).
Do you guys see Code issues with either the new main or tap box methods? I'm also seeing the possibility for utility restrictions on service size, configuration, and metering locations.
Thanks.
1) Assuming there is room in the gear, my Plan A would be to install a second line-side tap. I don't believe there's a any Code issue with this?
2) If there is no room in the existing switchgear, I don't believe I can add a tap-box in front of the switchgear because the existing 600A tap would become a tap of a tap, which is a violation?
3a) I'm thinking I can add a new main switchgear in front of the existing gear. Say a 5000A bus with a 3000A main, a 3000A branch feeding the existing switchgear and a 1600A branch feeding the new PV system. I'm not sure if this would strictly meet 705.12(D)(2)(3)(b)&(d).
Do you guys see Code issues with either the new main or tap box methods? I'm also seeing the possibility for utility restrictions on service size, configuration, and metering locations.