I encountered something that doesn't make sense to me in the field in a cooling tower room.
There is (1) 25HP blower motor and (2) 15HP pump motors being powered via a 3-phase 208V controller panel. Inside the control panel is a 3-pole 225A circuit breaker feeding all the motor loads mentioned. But a 3-pole 150 circuit breaker feeds the 3-pole 225A circuit breaker so in reality the whole circuit is limited by the 3-pole 150 amp circuit breaker.
Inside the control panel the 25HP is controlled by a VFD, the other (2) 15HP motors is not connected to the VFD and just being controlled by the contactors.
To size the breaker I take 2 times the largest motor FLC plus all the other FLC:
2*(74.8) + 48.3 +48.3 = 246.2A
Based on the calculation above a 250A circuit breaker is needed but how come the whole system is being powered by a 150A circuit breaker?
There is (1) 25HP blower motor and (2) 15HP pump motors being powered via a 3-phase 208V controller panel. Inside the control panel is a 3-pole 225A circuit breaker feeding all the motor loads mentioned. But a 3-pole 150 circuit breaker feeds the 3-pole 225A circuit breaker so in reality the whole circuit is limited by the 3-pole 150 amp circuit breaker.
Inside the control panel the 25HP is controlled by a VFD, the other (2) 15HP motors is not connected to the VFD and just being controlled by the contactors.
To size the breaker I take 2 times the largest motor FLC plus all the other FLC:
2*(74.8) + 48.3 +48.3 = 246.2A
Based on the calculation above a 250A circuit breaker is needed but how come the whole system is being powered by a 150A circuit breaker?