D dinkelja Member Oct 11, 2007 #1 Poll: What ampacity adjustment factor might you use on four multicondutor cables, each with four current carrying conductors?
Poll: What ampacity adjustment factor might you use on four multicondutor cables, each with four current carrying conductors?
D dinkelja Member Oct 11, 2007 #3 rr, I take that as you mean 50%. How about if I de-rated the conductors within the cables frist, then the group of 4 cables = 64% Any takers?
rr, I take that as you mean 50%. How about if I de-rated the conductors within the cables frist, then the group of 4 cables = 64% Any takers?
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Oct 11, 2007 #4 The rule has to do with the number of conductors, not the way the conductors are grouped.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Oct 11, 2007 #5 charlie b said: The rule has to do with the number of conductors, not the way the conductors are grouped. Click to expand... I agree,16 CCC's would require a derated value of 50%.
charlie b said: The rule has to do with the number of conductors, not the way the conductors are grouped. Click to expand... I agree,16 CCC's would require a derated value of 50%.