dinkelja

Member
Poll: What ampacity adjustment factor might you use on four multicondutor cables, each with four current carrying conductors?
 
rr, I take that as you mean 50%. How about if I de-rated the conductors within the cables frist, then the group of 4 cables = 64% Any takers?
 
The rule has to do with the number of conductors, not the way the conductors are grouped.
 
charlie b said:
The rule has to do with the number of conductors, not the way the conductors are grouped.


I agree,16 CCC's would require a derated value of 50%.
 